5/13/2011 2:08 AM | |
Joined: 10/7/2005 Last visit: 5/24/2024 Posts: 3007 Rating: (1049)
|
Hello jtemesy check if you have product release E01 of your AI card. If so, have a look at item 8 of the link below and see if you can get hold of an E02 relase or try a different "first" channel connection for your resistor: What measures do you need to take for error-free operation of the 6ES7 331-1KF0.-0AB0? If the above is not the case, have a look at the other suggested measures (unused channels, common mode voltage etc.) in the above link and see also the additional link below: With the correct wiring, how can you avoid exceeding the common-mode voltage (Ucm) and subsequent measured value overflow or underflow in the analog input module 6ES7 331-1KF0.-0AB0? I hope this helps and please let us know what you find. |
Cheers |
|
This contribution was helpful to2 thankful Users |