good day, look on the side of manual s7-300, Chapter 6 |
7/12/2013 3:48 AM | |
Posts: 139 Rating: (5) |
Hello, Normally, transducer is 2 wire connection (Loop power ) and in that case please check your Module Jumper (i think D mode) in hardware and in software module configuration you have to select 2DMU for this. If this is still in testing phase, then disable Channel Diagnostics and Test it out. please check attach for 2 wire and 4 wire connection. Attachment6ES7331-7NF10-0AB0.pdf (511 Downloads) |
Last edited by: C.kt at: 7/12/2013 3:52 AM |
|
7/12/2013 5:27 AM | |
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating: (9) |
Check the wiring again, sometimes its loose wiring that is the cause of problem. . |
7/12/2013 5:47 AM | |
Posts: 1064 Rating: (72) |
Check you plug on th eside and verify the setting |
7/12/2013 10:08 AM | |
Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
Hi Ayzetina, It is good practice to disable the unused channels. |
7/12/2013 4:08 PM | |
Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
Hi Ayzetina, Send us your connections and hardware configuration. |