3/25/2021 9:18 AM | |
Joined: 2/17/2009 Last visit: 1/26/2024 Posts: 4 Rating: (0) |
Dear Expert recently, I got several Analog Input failures on 7KF02 modules and I found some question on 4 wire wiring of it. All M- of 4 wire transmitters shall be tied into comp(10/11) of module and eventually it will tie with M of power for 2 wire. if 4 wire device make noise then all channels tie into Mana can be affected due to have same common point. Could you let me know why M- of 4wire has to be connected Mana appreciate you comment Mike ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/25/2021 11:39:41New subject after splitting |
|
4/11/2021 7:30 AM | |
Joined: 11/9/2017 Last visit: 5/4/2024 Posts: 151 Rating: (10) |
hi JH5 4 wire transmitter have separated power and analog signal cause for safety device for it, so u have 2 wire for power and 2 wire for analog signal, M- is 0V and Mana (M analog) need too connected to M- for loop connection |
If I could help you, be so kind and rate my contribution. :) |
|