4/26/2018 9:15 PM | |
Joined: 2/9/2016 Last visit: 5/28/2024 Posts: 56 Rating: (4) |
Hi, try this: https://www.youtube.com/watch?v=qbMUKpefvg0 M. |
This contribution was helpful to1 thankful Users |
4/26/2018 9:34 PM | |
Joined: 11/16/2012 Last visit: 3/10/2024 Posts: 307 Rating: (52) |
You need a media converter like this one Gigabit Single-Mode Media Converter MC210CS at each side. Then you can connect the LOGO!s with the media converter and the two media converter to each other with single mode fiber optic cable. |
Last edited by: MicTsc at: 4/26/2018 9:36:06 PMLast edited by: MicTsc at: 4/26/2018 9:37:40 PM |
|
This contribution was helpful to1 thankful Users |
4/27/2018 2:09 AM | |
Joined: 9/3/2008 Last visit: 5/27/2024 Posts: 923 Rating: (158) |
Hi k_ange The LOGOs do not have fiber optic connectors themselves, so you need a media converter, as already suggested, from RJ45 to fiber (one at each end). You mention a distance of up to 3.3 Km so a Multi mode fiber cable should be ok. This can go up to 5 Km. There are two Siemens Scalance media converters: SCALANCE X101-1 (6GK5101-1BB00-2AA3). Multimode, up to 5 Km SCALANCE X101-1LD (6GK5101-1BC00-2AA3). Single mode, up to 26 Km I hope this helps. |