11/11/2011 11:11 AM | |
Posts: 206 Rating: (22) |
Hi sysd_b, the easiest way to calibrate is with the Siwatool software, directly connected to the Siwarex M. In chapter 10 you find a discrption of Siwatool and the calibration. http://support.automation.siemens.com/WW/view/en/7787784/0/en If you want to do the calibration with Simatic only: 1. you have to change the data discribed in chapter 10.3 in the Siwarex DB data record 3 (DR3 2. send DR3 to the Siwarex FTA 3. Empty scale 4. execute command "zero point valid" no. 1 5. load adjustment weight to the scale 6. execute command "adjustment weight valid" no. 2 Then you are finished. Regards ABenno |
11/14/2011 11:53 AM | |
Posts: 206 Rating: (22) |
Hello sysd_b, how to send and receive DR and send command to the Siwarex M you can find in the manual chapter 5. http://support.automation.siemens.com/WW/view/en/7787784 e.g. read DR3 (S7 code) L 3 // DR no. T DB_SIWAREX.DBB53 L 1 // Set Bit 0 in bit field T DB_SIWAREX.DBW54 e.g.send DR3 (S7 code) L 3 // DR no. T DB_SIWAREX.DBB21 L 1 // Set Bit 0 in bit field T DB_SIWAREX.DBW22 e.g.sendcommand "adjustment zero valid" (S7 code) L1 //command code for "adjustment zero valid" see manual chapter 8 T DB_SIWAREX.DW88 L 1 // Set Bit 0 in bit field T DB_SIWAREX.DBW46 Regards ABenno |