7/11/2022 2:47 PM | |
Joined: 5/15/2017 Last visit: 5/9/2024 Posts: 11 Rating: (0) |
good evening all , i need advice . i have a project in which there a lot of danfoss fc302 drives connected in profibus to s7317-2pn/dp . even after downloading OB86 , the plc is going into stop mode whenever any one of the drive is powered off . is there any way to avoid this issue . the project is for a process factory which cannot afford plc going in to stop mode whenever a drive goes off . AttachmentTest.zip (535 Downloads) |
7/11/2022 3:48 PM | |
Joined: 4/24/2006 Last visit: 5/17/2024 Posts: 8649 Rating: (1151)
|
Hello, Do you still read and write to the drive that is disconnected? Best regards, Wizard |
7/12/2022 10:29 AM | |
Joined: 5/15/2017 Last visit: 5/9/2024 Posts: 11 Rating: (0) |
Thanks for the advice dchartier . i figured out where i went wrong and now the plc is fine .instead of going to stop mode there are sf and bf led on . the other issue i started facing is i added Ob32,40,82,83,5,86,87,121,122 to the program . when i compiled the charts all the ob's got deleted automatically . so i added all the ob's to a s7 tasklist .but after compiling and downloading , plc goes to stop mode only when drive comm is lost .if the et200s station is lost only sf and bf comes on. i have added the diagnose txt . if you could guide where am making mistake it would be great AttachmentDiagnose.txt (469 Downloads) |
Last edited by: aruns at: 07/12/2022 10:39:54 |
|
7/12/2022 10:38 AM | |
Joined: 5/15/2017 Last visit: 5/9/2024 Posts: 11 Rating: (0) |
i have also added the program backup and the diagnose in the zip file incase it helps. thanks
AttachmentTes1.zip (486 Downloads) |
2/24/2023 1:37 PM | |
Joined: 12/1/2022 Last visit: 3/12/2023 Posts: 6 Rating: (0) |
Thank you very much, your answer solved my problem! |