7/6/2013 9:13 PM | |
Joined: 8/27/2006 Last visit: 9/2/2024 Posts: 719 Rating:
|
On the module itself, do you see the red LED lighted?? if yes then it's an overrange, but I didn't think that injecting more than 20mA will give a result of zero. Did you check the jumper position on D (on the side of the module?
|
The more you know, The more you know that you don't know |
|
7/6/2013 9:25 PM | |
Joined: 5/28/2008 Last visit: 9/8/2024 Posts: 4515 Rating:
|
Result 0 is only on the HMI or SCADA But actually it gives him 27650 Counts So, it seems that he will check his SW. First he will check to increase high limit. |
Ayman Elotaify |
|
7/7/2013 2:18 PM | |
Posts: 28 Rating:
|
DearAyman Elotaify, I tried ur advise but unfortunately it doesn't work . let me tel u wat i did today... Checked complete attached card . CH1 27696 Unhealthy CH2 27608 Healthy CH3 27770 Unhealthy (Spare) I donno wat i need to do...it has OB40
|
7/7/2013 2:39 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating:
|
yes, you are right
Hello, Please attach your program here as said by our friend Amazing Ahmed. |
Last edited by: Amit_86 at: 7/7/2013 2:39 PMVANDE MATARAM..... |
|
7/7/2013 4:38 PM | |
Joined: 5/28/2008 Last visit: 9/8/2024 Posts: 4515 Rating:
|
Dear Mohammed,
|
Ayman Elotaify |
|
Follow us on