11/5/2010 12:48 PM | |
Posts: 5 Rating:
|
Can anyone help me? I would like to connect an MP277 HMI to a S5-135U PLC. What lead do I need? |
11/5/2010 3:04 PM | |
Joined: 4/24/2006 Last visit: 7/12/2024 Posts: 8711 Rating:
|
Dear JSMEL, Perhaps this manual might help: SIMATIC HMI WinCC flexible 2008 Communication Part 1 how is the connection between a Windows-based panel and a SIMATIC S5 set up? Best regards, Wizard |
This contribution was helpful to
1 thankful Users |
11/5/2010 4:21 PM | |
Posts: 5 Rating:
|
Wizard, |
11/5/2010 5:24 PM | |
Posts: 5 Rating:
|
The operating instructions do show an RS485 connection between the MP277 and the S5 processor. Thanks for your patience. Attachmenthmi_mp_277_operating_instructions_en-US_en-US[1].pdf (351 Downloads) |
1/6/2011 4:02 PM | |
Posts: 8946 Rating:
|
Hi Daniel, he also need some FB onto the S5 - CPU, does'nt? |
1/6/2011 4:19 PM | |
Joined: 4/24/2006 Last visit: 7/12/2024 Posts: 8711 Rating:
|
Dear IBN-Service, When you have a look at the manual: WinCC flexible Communication part 1. Link is in earlier post. See chapter 7.2.1.1. communication over AS511: "No special blocks are required on the PLC" See chapter 7.2.2.2. communication on Profibus DP: "you require the function blocks FB158 and FB159" (You can find on WinCC flexible DVD) Best regards, Wizard |
This contribution was helpful to
1 thankful Users |
1/6/2011 7:10 PM | |
Posts: 8946 Rating:
|
Thank you for confirmation, dear friend! |
This contribution was helpful to
1 thankful Users |