12/7/2017 4:38 PM | |
Posts: 15 Rating:
|
Dear Sir, kindly see attached file Do you have another Siwarex M module? yes, when i connected SF is off Can you exchange for a test the Siwarex M module? yes Maybe the Siwarex M module is damaged.... How i can repair it, shall i sent to Siemens? Which voltages (unit: VDC) can you measure at the Siwarex M module between the pins: - 19 and 17 ? -5VDC - 19 and 18 ? 48mVDC 0VDC - 20 and 17 ? +5VDC - 20 and 18 ? +5VDC Thanks, Amr Adnan Attachmentadjustment.pdf (447 Downloads) |