3/5/2023 5:11 PM | |
Joined: 3/3/2023 Last visit: 5/28/2023 Posts: 4 Rating:
hello i am new to programming i have a small hotel project with 20 rooms from each room i need to receive the status of an input and display (VISUALIZATION) this input status to the webserver (i will use the LOGO! of the main area as webserver) i thought to structure the network as seen in the attached images each room LOGO! to send via network input to a plc of the area and each AREA LOGO! to send to the main area LOGO!) is this achievable? all LOGO!s will be masters is there any limitation on communication? THANKS AttachmentIMAGES.zip (331 Downloads) |
3/5/2023 5:18 PM | |
Joined: 12/18/2014 Last visit: 8/12/2024 Posts: 33529 Rating:
That's possible. But I don't know what is the purpose of the flags? |
3/5/2023 5:27 PM | |
Thank you for the response I thought they were needed for visualization is there an alternative way?
3/5/2023 5:32 PM | |
You can show instead of the state of the flags the states of the NIs. |
3/5/2023 5:38 PM | |
I will try to modify it I used flags in lwe , as in block type it only shows the following options |
3/5/2023 5:43 PM | |
I will make you an example. |
3/5/2023 6:08 PM | |
You must allowed in all LOGO!s 8.3 the S7 access. |
3/5/2023 6:23 PM | |
Okay, you use the NIs and the NQs as remote setting, not as local memory. Then can you only use M flags. |
3/5/2023 6:29 PM | |
thank you for your help your advice was helpful i will be doing some tests in the next days
