Hello Nikhil017 Just to clarify -> Kepware is OPC DA (DCOM based) Server and communicates with S71500 with S7 communication? Then the S71500 has to use PutGeet -> work with non optimized DBs and activate the PutGetCommunciation in the security settings. S71500 can only act as OPC UA Server/Client by itself but not with OPC DA (DCOM) directly, so you need a OPC Server that can communicate with S7. Here a general Link for a full Siemens solution: https://support.industry.siemens.com/cs/ww/en/view/67295801 or: https://support.industry.siemens.com/cs/de/en/view/109474300 Bye Murof |