Hi Rvieira7, unfortunately i do not have a solution, but i found following FAQ. Which settings do you have to comply with in a PROFINET RT network in conjunction with VLAN switches?regards sancruz |
Feedback appreciated, please rate |
|
5/16/2023 7:28 AM | |
Joined: 10/7/2005 Last visit: 6/5/2024 Posts: 3008 Rating: (1051)
|
While PROFINET can be run in VLAN's as per sancruz advise and link, PROFINET IO data exchange is MAC address based and thus NOT routeable. What is possible is to use the I-Device PLC as an IO Controller instead and add a PN/PN coupler (in which case each IO Controller has their own independent Network and IP address range) See also Is cross-subnet PROFINET IO communication possible for more. |