The Bükert SE30 is a frequency pulse output module that is not compatible with a 0/4-20mA analog input module. The screen shots of the wiring diagrams (Figures 7 and 8) from the operating manual at https://www.burkert.com/en/type/SE30 shows the SE30 wired to a "pulse input on external instrument", not to an analog input on external instrument. A pulse input is typically a 24Vdc discrete input module capable of being able to count up to 300Hz, the number of pulses/second coming from the flow meter at the max flow rate. To interpret the pulses/second to pulses/liter you'll need the flowmeter's K-factor, but the K-factor is not in the operating instructions. Page 10 of the instruction manual says, "The conversion coefficient (K-factor) expressed in pulses per litre is given in the Operating Instructions of the sensor-fitting type S030 used, available at: country.burkert.com |
This contribution was helpful to1 thankful Users |
6/13/2023 1:42 AM | |
Joined: 3/28/2010 Last visit: 11/14/2024 Posts: 1074 Rating: (214)
|
Is it also possible to connect it to DQ 8x24VDC 0.5A ST? Answer: No, there's no way a DO card can read discrete input. Alternative: Signal condition There are stand-alone signal conditioners, pulse-frequency-to-4-20mA current, that can convert the 0-300Hz signal from the flow meter to 4-20mA. One in the USA is https://api-usa.com/pdf/api/api7010g.pdf You can use words from the spec sheet to find one in your part of the world. |
This contribution was helpful to3 thankful Users |
6/13/2023 4:57 PM | |
Joined: 4/20/2023 Last visit: 10/9/2024 Posts: 33 Rating: (0) |
Thank you very much. I meant DI. It was a typo. I got it. thanks for the time. |
Follow us on