Joined: 5/29/2013 Last visit: 6/26/2024 Posts: 29 Rating: (0) |
Hello, I guess its the same topic We have attached the CP343-1 to 315DP plc (checked in the manual, it is supported). The whole network is green and all devices are seen. As we understood we have to use PNIO_RECV block to receive the data. We have configured it as per manual and also checked data area ranges, all seems to be fine Still getting the error 8184 and nothing else we can do Thank you in advance ------------------------------------------------------------------------------------------ AttachmentDownloads.zip (281 Downloads) |
Last edited by: The Helping Hand at: 02/15/2024 08:51:38New subject after splitting and text formatting optimized |
|
2/15/2024 9:02 AM | |
Joined: 2/24/2011 Last visit: 9/26/2024 Posts: 58 Rating: (5) |
please note: 1. the FAQ "How do you program communication blocks FC11 and FC12 for the PROFINET IO controller?" https://support.industry.siemens.com/cs/ww/en/view/26558253 2. the possible status codes in the STEP 7 Help viewer of the used block Status 0x8184 is system error or bad parameter types. So you have to check the used data types of the IN(OUT parameter and the diagnostic buffer of the CP and CPU. |
Last edited by: The Helping Hand at: 02/15/2024 09:12:53Link and text formatting optimized Last edited by: The Helping Hand at: 02/15/2024 09:13:36 |
|
This contribution was helpful to1 thankful Users |