Siemens S7 400 NetPro connections stop communicating when the plant is not in production for a while. We have to redownload NetPro connections to reestablish comms. What can cause this, and how do I rectify the issue? See attachments for NetPro healthy and unhealthy statuses. AttachmentLine 1 LCC1 NetPro healty and unhealthy statuses.pdf (666 Downloads) |
8/10/2024 9:44 PM | |
Joined: 1/31/2022 Last visit: 11/13/2024 Posts: 7 Rating: (0) |
Resolved the issue by replacing CP443-1 card. |