Hello, Both the PUT and the GET must be located in the PN-CPU, using the connection ID found in Netpro in the PN-CPU (In your configuration the PN-CPU is the only one that can have initiative, it is the S7 Client.). No program at all in the CPU with CP-Lean (it acts as an S7 server, it can only react to requests of the partner). Usage of PUT and GET can be found here: http://support.automation.siemens.com/WW/view/en/18610307 |