11/15/2012 3:49 PM | |
Joined: 7/7/2010 Last visit: 10/18/2024 Posts: 15327 Rating: (2432)
|
What is the MIRS LED? If it is the maint led, it sounds like the firmware update did not complete properly or is still needing at least one more power cycle. Follow the firmware update procedure exactly and conservatively as some steps take longer than you might think. Once that happens, you can try the primary setup tool (PST) found here: https://support.automation.siemens.com/WW/llisapi.dll?query=s7-1200+setup+tool+download&func=cslib.cssearch&content=adsearch%2Fadsearch.aspx%3Ftab%3D2&lang=en&siteid=csius&objaction=cssearch&searchinprim=_searchinprim_&nodeid=99&x=16&y=8&cssearchengine=NEW If it can see the plc, go ahead and set the ip address manually. If it cannot see the plc, the firmware update needs to be done again. After you get it working again, you may want to do a memory reset and then update and download your project. By update, I mean to update the plc device to firmware 2.2 in the project so it matches the hardware device's firmware. Post your results. |
science guy |
|
11/16/2012 2:29 PM | |
Joined: 8/31/2010 Last visit: 10/15/2024 Posts: 1522 Rating: (228) |
Hello The Android, Download this S7-1200Tool.zip ( 55566 KB ) Try to find the CPU under Accessible Device, for procedure follow this FAQ - How can you change the IP address of an S7-1200 without using STEP 7 Basic? |
Like it? Rate it! |
|
This contribution was helpful to1 thankful Users |