10/27/2011 5:03 PM | |
Posts: 126 Rating:
|
DHCP is not supported on the S7-1200 PLC. Currently it can be hardcoded, configured by T_CONFIG or downloaded by the Profinet DCP protocol. Sorry. John |
8/15/2013 1:46 PM | |
Posts: 1 Rating:
|
We are in a similar situation. I would very much like to know how I can reliably change the IP address of my STEP 7 1200 PLC. Thanks! |
10/20/2014 5:45 PM | |
Joined: 3/17/2014 Last visit: 8/31/2021 Posts: 31 Rating:
|
Hi, is this still that way? is DHCP not available for s7-1200? Thanks.
|
10/21/2014 11:31 AM | |
Posts: 1368 Rating:
|
jepp...still the same with S7-1200 CPUs... |
10/21/2014 12:16 PM | |
Posts: 1368 Rating:
|
plcs does not support this function. CPs I think supports DHCP |
This contribution was helpful to
1 thankful Users |
Follow us on