11/12/2018 5:18 AM | |
Posts: 87 Rating: (0) |
Hello to all, Can someone help me with following issue. Well, i can download HMI program to the panel, but when the runtime is activated, all fields are filled with "####". Also, when i start simulation from the lap top i can see that. In attachmen are some pictures about versions and how i connected. Thanks in advance. Regards, Attachment3.zip (48 Downloads) |
11/12/2018 6:59 AM | |
Posts: 87 Rating: (0) |
Thank you for the answer, but i have already assigned PG/PC interface to LAN1 where I put profinet cable. Regards, M |
11/12/2018 7:10 AM | |
Posts: 87 Rating: (0) |
I found it. The problem was in Access point. Should be defined as S7ONLINE and in my project was S7ONLINE1. Regrads, M |