Hello GUWS; A S7-1200 supports Profinet and Modbus TCP concurrently on its integrated Ethernet port (as well as many other protocols), as seen in this FAQ; https://support.industry.siemens.com/cs/mx/en/view/38051505 Basically, the switch you select should be transparent to your Ethernet exchanges, in this case. What model is your SCALANCE switch? An unmanaged switch will allow both protocols to transit without any configuration. A more complex (managed) switch may require you select authorized ports for the different protocols you want to use. Hope this helps, |