I am having problem migrating the project from SIEMENS OP277 HMI panel to KP 700 comfort Panel. The original backup is in WinCC flexible 2008, SP2. Please guide ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/26/2020 14:00:58New subject after splitting |
|
9/7/2020 2:16 PM | |
Joined: 8/3/2009 Last visit: 8/6/2024 Posts: 13467 Rating:
|
Hello If you do not have WinCC flexible and TIA on the same system then you can use the TIA Migration Tool. you need at least WinCC Comfort check this Migration guide: https://support.industry.siemens.com/cs/ww/en/view/49752044 You wrote "Backup"...?? if you only have a Backup from the Panel without the WinCC flexible Project then you cannot transfer it to Comfort Panel, only with this special Solution: https://support.industry.siemens.com/cs/de/en/view/109765132 If this hints do not help, then please give us more information... Bye Murof |
Last edited by: Murof at: 09/07/2020 14:18:54Last edited by: Murof at: 09/07/2020 14:19:29If this Information really helps, you could use the Rate function |
|