4/6/2013 7:41 PM | |
Joined: 1/3/2006 Last visit: 2/19/2024 Posts: 726 Rating:
|
Hi Just in case if anyone needs to confiugre the Easygen data,I have attached the excell sheet which can help calcualte the the DB structure as per data structure of Easygen. Well just in case if anyone is wondering what the starting Modbus address of eaygen is, then answere is:C350 (hex). It took me horribly long time to figure out the start address of it. Wondering why does all modbus enabled devices has different starting address? AttachmentEG 3000 Interface.zip (1183 Downloads) |
This contribution was helpful to
2 thankful Users |
1/2/2015 9:32 AM | |
Posts: 3 Rating:
|
Dear Saravana Kumar, We are doing as you do on 2009. We need connect s7-300 withCPU314 and communication moduleCP341 and Modbus RTU Easygen 3000. Could you send me your draft Step7 for CP341 and RS-485 Easygen 3000 communication? As register address rangesfor visualizationof easYgen 3000 higher than 50000, but our module CP341 only read under 50000. Regards LHN Dear Saravana Kumar, Happy New Year! Attached are files: - communication manual of easYgen 3200 ( will upload later into 2 parts) - S7300 CPU314-CP314 Modbus master operating instruction. Best regards LHN
Attachments7300_modbus_master_operating_instructions_en-US_en-US.pdf (818 Downloads) |
1/2/2015 10:31 AM | |
Posts: 3 Rating:
|
Dear Saravana Kumar, Attachedfile: - communication manual of easYgen 3200 ( data protocol 5010) Best regards LHN
Attachment37472 - easYgen-31003200 Interface Manual, Data protocol 5100.pdf (788 Downloads) |
1/2/2015 10:33 AM | |
Joined: 2/6/2009 Last visit: 8/2/2024 Posts: 939 Rating:
|
Dear LHN, We have done the communcation by trails and error method only. Please find the attachment for the Send list and Receive data's of Woodward 3000 modbus device with CP 341. AttachmentWoodward.zip (802 Downloads) |
_______________________________________________________________ |
|
Follow us on