12/15/2014 9:54 AM | |
Posts: 211 Rating: (6) |
Sorry, but you did not answer my question. Beste regards, |
12/15/2014 11:00 AM | |
Posts: 1368 Rating: (126) |
LLDP is only necessary for PROFINET functions based on topology. To use PROFINET with the RT class "RT", you can use any switch of "PROFINET Conformance Class A" or higher. All switches of the SCALANCE product family meet these requirements. If you want to use PROFINET functions that provide an additional value, such as topology recognition, diagnostics, device exchange without exchangeable medium/programming device, you have to use a switch of the "PROFINET Conformance Class B" or higher. |
Last edited by: Pittiplatsch at: 12/15/2014 11:06 AM |
|
12/19/2014 8:22 AM | |
Posts: 211 Rating: (6) |
Hi, Fafner. Update times are in seconds (2sec is OK for me). |
12/19/2014 8:33 AM | |
Joined: 3/20/2013 Last visit: 4/3/2024 Posts: 676 Rating: (43) |
go for it. |
Best Regards, |
|
12/19/2014 8:40 AM | |
Posts: 211 Rating: (6) |
Thanks! And can you tell me anything about integrating such system in a higl-level system, see topic here: Mixing different types of switches Did you try that? Thanks! |
Last edited by: Homeroid_BL at: 12/19/2014 8:41 AM |
|
12/23/2014 8:41 AM | |
Joined: 3/20/2013 Last visit: 4/3/2024 Posts: 676 Rating: (43) |
|
Best Regards, |
|