2/23/2010 2:12 PM | |
Posts: 8 Rating: (0) |
Hello, We are looking for a SIL2 encoder to process in our S7-400FH system. We found a model that supports Profisafehttp://www.twk.de/data/pdf/11947fe0.pdf. It also supports distributed safety 5.4 so he is compatible with the S7-300F systems. But we want to know if the encoder is also compatible with a S7 - 400FH system. Has anyone used this encoder or shed some light if an device is compatible with profiSafe it can be used in a 400F system? Regards, Skier
|
3/4/2010 11:54 AM | |
Posts: 8 Rating: (0) |
Hello, In atachment also the GSD file. I can't find a reference to CRC 7 in it. Regards, Skier
AttachmentSAFEC24S.zip (938 Downloads) |
3/8/2010 5:08 PM | |
Joined: 4/17/2009 Last visit: 10/23/2024 Posts: 304 Rating: (57)
|
Hello Skiertje The CRC7 is defined in IEC 61784-3-3:2007 chapter 8.4.1 as "Securing the Safety I/O data". This CRC is required for usage with 400 F/H. It's termed: “F_IO_StructureDescCRC” = CRC7. In accordance to the attached TWK GSD, it seems to be integrated. But we take no guarantee for this. Best Regards SET-Team Attachmentpages from s7fssysb_V6.1_Configuring fail-safe DP standard slaves.pdf (963 Downloads) |
SE Support |
|
This contribution was helpful to1 thankful Users |
12/31/2015 2:03 PM | |
Joined: 9/1/2005 Last visit: 11/18/2024 Posts: 4113 Rating: (195) |
New question published by AutoGen_999280 is split to a separate thread with the subject monitoring a speed of the process with ET200SP. Best regards |