(0)| 1/1/2022 7:35 AM | |
|
Posts: 1 Rating:
|
I am communicating with energy meter em6436H as well with MODSCAN software, trying to read voltage from energy meter and it shows all max values i.e 6423 And also i have tried using arduino using rs485 and it also does not read the voltage. please help me out if anyone know how to do ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 01/03/2022 09:42:59New subject after splitting |
|
| 1/3/2022 9:57 AM | |
|
Joined: 6/19/2019 Last visit: 10/24/2025 Posts: 743 Rating:
|
Hello, Did you realy read correct address and it's float32 data type? See table with modbus addresses: |
| 2/23/2022 7:18 AM | |
|
Posts: 1 Rating:
|
Note that you have to use Swapped Floating Point in MODSCAN to get the correct values. |