(3)| 7/30/2021 5:02 PM | |
|
Joined: 2/22/2008 Last visit: 4/25/2025 Posts: 2698 Rating:
|
If the Modbus registers also have floating point values, it would be easy to integrate them in the Logo controller with the F/I Converter incl. scaling 0.001, 0.01, 0.1, 1, 10, 100, 1000. If you only have UINT32 (unsigned integer with 32 bit), then you can use the attached converter. Of course, if you have greater values than 32767, then you lost the last 1-3 digits depend of your max. values. Maybe it's also possible to create an converter from SINT32 (signed integer with 31 bit plus sign), but often this makes no sense. Regards, Scorp AttachmentUINT32_SINT16.zip (1112 Downloads) |
This contribution was helpful to
|
|
| 9/23/2021 8:36 AM | |
|
Posts: 3 Rating:
|
Could you send us another time? When unzip then I open with LOGO! App V8 an error pop up! Attached image. |
| 9/23/2021 8:41 AM | |
|
Joined: 12/18/2014 Last visit: 12/25/2025 Posts: 36371 Rating:
|
Here's a version for LSC V8.0.
AttachmentUINT32_SINT16_0BA8.Standard.zip (1070 Downloads) |
This contribution was helpful to
|
|