(0)| 12/10/2020 1:54 PM | |
|
Posts: 3 Rating:
|
Hi All, Please find attached photo which I use in my system, Please I need know how to connect this system together, I try many time, i see many Error and Wrong alarm.
------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/10/2020 15:46:02New subject after splitting |
|
| 12/16/2020 6:48 PM | |
|
Joined: 1/28/2014 Last visit: 12/16/2025 Posts: 90 Rating:
|
Hi mohd mahd, Basically, you have to follow the following steps: 1. Insert S7-1500R/H System and periphery (In network view you can see S7 1500 system coupled). 2. Multiassign IMs to S7 1500R/H sytem. 3. Connect Basic Panel to one S7 1500 X2 port. (Basic Panel connects via System IP). 4. Enable System IP. See attached Screenshots You can find more information in SIMATIC S7-1500 S7-1500R/H redundant system manual https://support.industry.siemens.com/cs/ww/en/view/109754833 AttachmentS71500RH.zip (714 Downloads) |
|
If you find the information useful, I would appreciate your rating |
|
This contribution was helpful to
|
|