5/2/2008 10:18 PM | |
Posts: 2661 Rating:
|
Are using the appropriate MTA? |
5/3/2008 7:35 PM | |
Joined: 1/20/2008 Last visit: 9/6/2025 Posts: 120 Rating:
|
Thank you Phantom and Late I have not MTA in my project. |
5/4/2008 8:10 PM | |
Joined: 1/20/2008 Last visit: 9/6/2025 Posts: 120 Rating:
|
Thank you Late : I used FC451 in OB1 and OB35. But when one of the AO modules fails, the other one give half value again. |
5/5/2008 1:56 AM | |
Posts: 2661 Rating:
|
MRG: I looked at your program and did not notice anything wrong in the blocks. However, you should make a couple of changes in HW config: a) Set the OB35 to PIP1 (for example) and also set this PIP for the AO's. b) Change OB85 option in CPU properties. It is described in the attached document. Also, make sure the wiring is ok. Just as a reminder, in redundant I/O only lower address is relevant in the user program. All the best, Phantom AttachmentDokument1.pdf (1063 Downloads) |
5/5/2008 11:19 AM | |
Posts: 12 Rating:
|
Pls try calling Red Diag block in OB82 as well. |
5/8/2008 6:47 PM | |
Joined: 1/20/2008 Last visit: 9/6/2025 Posts: 120 Rating:
|
Secound module is active and ok in power and connection. |
5/9/2008 5:24 AM | |
Joined: 1/20/2008 Last visit: 9/6/2025 Posts: 120 Rating:
|
Also for DI and DO, redundancy work correctly. |
Follow us on