4/12/2012 2:31 PM | |
Posts: 24 Rating:
|
Hi LOGO! user's, I want to connect a siemens logo! 0BA7 with a S7-300. It's possible ? Do you have an example ? Thanks, Greg, |
4/12/2012 2:47 PM | |
Posts: 2930 Rating:
|
Hi, I only know of a example LOGO! 0BA7 and S7-1200 with TIA Portal, but should be simmilar with S7-300 and Step 7. The example you can find here: Hope it helps |
4/12/2012 2:49 PM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Yes it can be done, you need to make a S7 connection, see: /tf/WW/en/Posts/63134 That is for a 400, should be almost the same. And have a look at the logo examples, not for a 300 but makes things about the communication maybe a bit more clear. https://www.automation.siemens.com/mcms/programmable-logic-controller/en/logic-module-logo/application-examples/Pages/Default.aspx Regards, Marcjan |
Last edited by: Marcjan at: 4/12/2012 2:50 PMAnd i should type faster :-) Problem solved? |
|
4/12/2012 2:56 PM | |
Posts: 24 Rating:
|
Ok thanks. I also want to work with wincc. It is possible to simulate this with plcsim and logo! soft comfort ? |
4/12/2012 3:17 PM | |
Posts: 24 Rating:
|
(wincc explorer) |
4/13/2012 7:28 AM | |
Posts: 26 Rating:
|
Hi This information can be useful http://www.automation.siemens.com/salesmaterial-as/software/applications/logo/hmi_communication_wincc_flexible.zip AttachmentEN_HMI-communication_(WinCC_flexible).pdf (714 Downloads) |
Last edited by: Andres Str at: 4/13/2012 7:37 AMI can''''t refer the active |
|
4/13/2012 11:34 AM | |
Posts: 24 Rating:
|
I have some problems to choose the V0.0 in the wincc parametersusing in the logo soft comfort. |
4/13/2012 11:36 AM | |
Posts: 24 Rating:
|
I can choose DB,MW,EW,Aw,Z,T, but not the V unit |
4/13/2012 12:50 PM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, I think you have to make an OPC connection, then it might work like S7-200 PLC. http://support.automation.siemens.com/WW/view/en/21918337 Regards, Marcjan |
Problem solved? |
|