Hello! I have read a lot of topics on this forum, but I have not found a solution to the problem. When trying to initialize the modbus port, I get error 16 # 7000. In this case, the DONE bit at the first initialization is set to one, but then it is again transferred to FALSE. The error bit is not true. I use 1215C DC/DC/RLY CPU (Firmware v 4.4) and CB 1241 board (v 1.0). TIA Portal V16 with 4.4V of MODBUS(RTU) lib. COMLOAD v 3.1 and MASTER v 3.3 with cleear project from example. What can i do wuth it? I set MODE to 4. |
Last edited by: Jen_Moderator at: 04/15/2021 11:14:24Optimized link. |
|
| 4/15/2021 8:29 AM | |
|
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
|
Hello,
I recommend for first read Help about your mentioned block. Then you can see that in STATUS values description some values with ERROR value indicate no error but only status. Check pls what your value indicate and you can then be sure you haven't error. In many topics is clear that output signals can be available only for one scan of CPU so you need monitor them in code to be sure all is working ok because after scan passed your value can be set to FALSE. Hope you understand why you set MODE to 4, simply read pls Help what each of parameters means and what values can be set. |
Last edited by: Duris_I at: 04/15/2021 08:31:06With best regards... |
|
| 4/16/2021 10:29 AM | |
|
Posts: 11 Rating:
|
Now, i just change CB1241 to CM1241 and my data transmittion works right. All settings are same. |