(1)| 7/8/2021 3:11 PM | |
|
Posts: 7 Rating:
|
i have pressure transmitter wika :specifications ,3wire,signal (4 To 20ma ) ,power : 24vdc How install this instrument at analog module (6ES7331-7KF02-0AB0) Thanks |
| 7/8/2021 3:43 PM | |
|
Posts: 5521 Rating:
|
hi, 3-wire-transducers are like 4-wire-transducers with a combined M. so Measuring range module should be set to C. Wiring is described here: Analog input module SM 331; AI 8 x 12 bit;(6ES7331-7KF02-0AB0) 24VDC of the sensor is clear. The one wire for measuring goes on "+" of the chanel and the "-" of the chanel goes to M of the same potential of the power-supply of the sensor. hope this helps, regards, |
This contribution was helpful to
|
|
| 7/9/2021 12:46 PM | |
|
Posts: 7 Rating:
|
Thanks |
| 7/9/2021 12:58 PM | |
|
Posts: 7 Rating:
|
|
Follow us on