(0)| 9/1/2021 7:41 PM | |
Posts: 26 Rating:
so i have to upload the project from the panel ? |
| 9/1/2021 7:50 PM | |
Joined: 12/18/2014 Last visit: 12/31/2025 Posts: 36386 Rating:
Protool V6.2? To my knowledge is the last version V6.0 SP3. |
| 9/1/2021 8:15 PM | |
Joined: 5/12/2006 Last visit: 12/19/2025 Posts: 22816 Rating:
you can't |
| 9/1/2021 8:21 PM | |
Joined: 3/28/2015 Last visit: 12/30/2025 Posts: 727 Rating:
Hello,
When the original program was downloaded to the HMI and an option "Enable Back Transfer" checked,you can upload the program with the Protool software and open/edit it but this require a large memory which is not available in such panels. Otherwise,you can backup the program using the Prosave software but this backup can be downloaded to the same type of panel and not able to open/edit it. |
Eng.Mohamed Ibrahim |
| 9/2/2021 9:36 AM | |
Posts: 26 Rating:
ixo65 i pressed 2 instead of zero by mistake you are right |
| 9/3/2021 1:30 PM | |
Posts: 26 Rating:
if i insert this memory card in another tp 170p panel would the project work on the panel ? |
| 9/3/2021 8:28 PM | |
Hello, If you restore the memory card into a same type of panel,it should work. |