(2)| 8/24/2021 4:57 PM | |
Posts: 11 Rating:
i don't understand what is the problem |
| 8/25/2021 8:42 AM | |
Posts: 11 Rating:
Has anyone had such a problem? |
| 9/4/2021 4:39 PM | |
Joined: 9/27/2006 Last visit: 12/31/2025 Posts: 12479 Rating:
Hllo Spport; The first 2 pictures you showed are for 2 different CPUs, one promary and one standby? I ask because both pictures present an active LED Rack 1; in a redundant system S7-400H one CPU should be rack 0, the other rack 1. It seems that both racks are operating in stand-alone mode, which can cause all knds of errors, since for example you should not have the synchonization modules active and connected on the CPUs in this case. I suggest that as a first step you choose one CPU as primary and set it as rack number 0, usig the switch at the back of the CPU module. This is shown in the screenshot belw, taken form the S7-400H v4.5 manual: https://support.industry.siemens.com/cs/ww/en/view/1186523 We can then start looking at other issues you are facing. Daniel Chartier |
This contribution was helpful to
| 9/6/2021 6:16 PM | |
Posts: 11 Rating:
Thank you for your interest. yes 2 pic. same please look video AttachmentWhatsApp Video 2021-06-29 at 14.14.57.wmv (610 Downloads) |