(0)| 11/17/2021 10:33 AM | |
Joined: 3/2/2007 Last visit: 1/12/2026 Posts: 1000 Rating:
Kindly, which absolute encoder can we use with the s7-1500t plc ? We need this encoder to be the "synchronous angular position" master of several 1fk7 axis . Do you have some Siemens order numbers for this type of encoder ? 6ES7516-3TN00-0AB0 , SIMATIC S7-1500T, CPU 1516T-3 PN/DP, Central processing unit with 1.5 MB RAM for program and 5 MB for data, 1st interface: PROFINET IRT with 2-port switch, 2nd interface, Ethernet, 3rd interface, PROFIBUS, 10 ns bit performance, SIMATIC Memory Card required https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10339974?tree=CatalogTree |
... thank you ... |
| 11/17/2021 3:51 PM | |
Joined: 10/11/2006 Last visit: 1/8/2026 Posts: 6065 Rating:
Hello, I would use a sin/cos encoder becasue the higher resolution and connect to the Sinamics CU320-2. SINAMICS S120 and SIMATIC S7-1500(T): How to connect a 2nd encoder via Startdrive to the TO_ExternalEncoder https://support.industry.siemens.com/cs/de/en/view/109793754 Encoder see chapter 11; https://support.industry.siemens.com/cs/de/en/view/109747019 |
With best regards, |
| 11/18/2021 12:08 PM | |
Hello, the encoder suits. 3 PROFINET/PROFIBUS encoder https://support.industry.siemens.com/cs/de/en/view/109486133 For load calculation of S7-1500 CPU, you can use TST, |