(2)| 2/22/2022 10:53 AM | |
|
Joined: 4/24/2006 Last visit: 1/8/2026 Posts: 9104 Rating:
|
Hello, Depends on the following: Why do you need an Ethernet interface? Have a look here: What differences are there between the Industrial Ethernet CPs of SIMATIC S7-300? Best regards, Wizard |
| 2/22/2022 10:56 AM | |
|
Joined: 7/9/2015 Last visit: 1/7/2026 Posts: 4493 Rating:
|
Hi, you can use CP343-1 but please check if your S7-312 PLC is compatible to it. Check manual of CP - in Chapter 3 you will find a Table with which PLC the CP can be used. SIMATIC NET: S7-300 - Industrial Ethernet / PROFINET CP 343-1 - part BRegards, Towome |
|
|
|