Search on WAGO web sites. |
8/18/2022 1:39 PM | |
Joined: 9/27/2006 Last visit: 9/2/2025 Posts: 12396 Rating:
|
Hello mehakkk; https://www.wago.com/ca-en/plcs-controllers/controller-ethernet/p/750-843 If you examine the technical data found in the webpage above you will see that this 750-843 fieldbus module is designed for Modbus TCP connections, and there are no gsd files for such a module. The following article from Profinetuniversity.com explains the use of a gsd(ml) file in a Profinet network. Modbus/TCP does not use this tool. https://profinetuniversity.com/profinet-basics/profinet-gsd-file-basics/ Hope this helps, Daniel Chartier |