(1)| 10/23/2022 1:19 PM | |
|
Posts: 14 Rating:
|
here is the program for the logo and for the tia portal
Attachmenttiaportal_warsztat_zip.zip (724 Downloads) |
| 10/23/2022 2:50 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
I'm sorry, but I can't open the TIA project because I have only TIA V16. |
| 10/23/2022 3:29 PM | |
|
Posts: 14 Rating:
|
Is it possible to downgrade a project from v17 to v16 ? |
| 10/23/2022 3:37 PM | |
|
Joined: 12/18/2014 Last visit: 1/10/2026 Posts: 36432 Rating:
|
In attachment a simple example in TIA V16. This can you open with V17. Control the settings in the in the HMI tags. The values from the LOGO! must have the data format "Int" In you LOGO! program you read with a NAI the address VW2 and then connect you the NAI to the analog amplifier B014. In B014 you set a offset of -498 and connect the output to a NAQ with the address VW130. In this case has the VW130 the value of -498. I think you have select in the HMI the data format "Word". AttachmentKTP400.zip (734 Downloads) |