(1)| 12/23/2016 8:05 PM | |
|
Posts: 110 Rating:
|
Hi experts, I have a problem in site...PLC panel was working perfectly for one year after that there was a short circuit in the next cabinet of PLC . then PLC and IM rack showing SF and BF fault now we have downloaded the original backup to PLC and still showing the error we have tried the following methods 1.changed profibus cable 2.changed dp connector while online it is showing "dp slave not ready for data exchange yet" also I have attached the diagnostic buffer and system pic please guide to troubleshoot this issue AttachmentDiagnose.txt (1222 Downloads) |
Last edited by: sandy1984 at: 12/24/2016 6:44:06 AM |
|
| 12/23/2016 8:35 PM | |
|
Posts: 623 Rating:
|
Hi, There is no comm. between PLC and IM so OB122 is called by system[BF LED]. There is SF fault on IM so chek by replacing IM. |