(0)| 6/6/2023 11:41 AM | |
Joined: 3/11/2019 Last visit: 1/7/2026 Posts: 1653 Rating:
Hi Zubair, this table may be helpful. There you can see the analog representation of the different measuring ranges. Measurement ranges of the analog inputs for voltage and current (SB and SM)-> first table "Voltage Measuring Range" regards sancruz |
| 6/6/2023 4:20 PM | |
Joined: 3/30/2020 Last visit: 12/11/2025 Posts: 5656 Rating:
Suggestion: Get an amplifier that can amplify the 100mV to 10V. A company such as Phoenix Contact has them. Search delivers: [link] or specifically [link]. Have the amplifier installed as close to the field device as you can to better the noise immunity. A 4-20mA signal to the PLC would have been better. Consider a converter to communications if the distance between PLC and device is too big. |