(0)| 10/21/2023 8:11 AM | |
|
Posts: 3 Rating:
|
Hi, I am using PT-100 3 Wire with USB Temp Transmitter on top of it converting Temp in Mili volts. Can I use the same with the Example provided in above with my LOGO PLC and on which ports do I have to connect it ? Please guide. For you information I have downloaded the Code in LWE and it is running fine with my LOGO Plc. I am using this transmitter https://cdn.novusautomation.com/downloads/manual_txblock_transmitter_usb_4-20ma_v10x_o_en.pdf. Please guide on which ports should i connect two wires of + and - to measure Mili Voltson Logo PLC using your above example and LWE. Thanks in Advance. Shaan. ------------------------------------------------------------------------------------------ Attachmentmanual_txblock_transmitter_usb_4-20ma_v10x_o_en.pdf (519 Downloads) |
Last edited by: Jen_Moderator at: 10/23/2023 10:22:30New subject after splitting. Quote inserted. |
|
| 10/21/2023 11:06 AM | |
|
Joined: 12/18/2014 Last visit: 12/31/2025 Posts: 36391 Rating:
|
Which LOGO! model have you exactly? Please write the complete order number. |
| 10/24/2023 6:29 AM | |
|
Posts: 3 Rating:
|
LOGO PLC Model : Siemens LOGO 12/24RCE (6ED1057-3BA01-0AA8) Order: 21015879 Placed on 10/21/2021 through Wiautomation.com Thanks. |
| 10/24/2023 6:36 AM | |
|
Joined: 12/18/2014 Last visit: 12/31/2025 Posts: 36391 Rating:
|
Which AI address want you to use? AI1 (Pin I7)? |
| 10/24/2023 6:44 AM | |
|
Joined: 12/18/2014 Last visit: 12/31/2025 Posts: 36391 Rating:
|
In attachment a solution for AI1 (Pin7). The power supplies of the transmitter and the LOGO! must be the same 24 VDC. AttachmentUntitled.pdf (601 Downloads) |
Last edited by: ixo65 at: 10/24/2023 06:44:54Attachment |
|