(0)| 12/29/2023 8:26 AM | |
|
Posts: 8092 Rating:
|
Hello, BTW which is CU unit? p2000 rpm, p2001 Vrms, p2002 Arms, p2003 Nm etc. etc. are reference values which units can be select by p0505 which are in ratio to their values set in respective parameters. User need to output values in % of reference values by setting parameters & as per logic requirement, e.g. 4000H = 100% for WORD type & 4000 0000H = 100% = DOUBLE WORD e.g. if p2000 = 1500 RPM then value displayed in r0021 is in RPM which is scaled to value set in p2000 same with current i.e. motor current r0027 is displayed in Arms which is calculated value scaled to value set in p2002. In PLC user need to convert these values as per requirement e.g. as reference values in % or real values as per data received from drive. For more details please refer below manuals. SINAMICS G120 Control Units CU240B-2/CU240E-2 SINAMICS G120 Control Units CU250S-2 SINAMICS G120 CU230P-2 Control Units Hope this helps. |