(0)| 1/5/2024 11:27 AM | |
|
Joined: 4/28/2009 Last visit: 6/3/2025 Posts: 347 Rating:
|
Hello, if I understand correctly, before, with first or second drive connected to safety signals it works correctly. After dividing signals to both drives it stopped to work. And although you meassure 24V on DI (agains COM terminal) drive didn't show ON status on DI in parameter p722. According to attached circuit diagrams, there is no problem with dividing of safety signals to two drives. The only thing in circuit I forgot, is interconnection between M terminals on both drives and 24V power supply. Then the only thing I can think of is, could the some peak voltage have gone to DIs or drive ground and destroyed them? Did you check whether DI4 and DI5 work as standart inputs (disconnected from safety circuits)? With regards Martin Attachmentdiagrams.zip (366 Downloads) |