Hi, Overvoltage is measured in the DC-Link, and occurs when the DC-Link voltage is to high. Please control your ramp times (P2257 / P2258) and the PID- setup like Kp (P2280), D (P2274), Tn (P2285) ------------------------------------------------------------- Why do you want to use PID-Control? Why you don’t use fixed frequencies? Witch signal you are sending to PID? Do you using a temperature sensor which switches ON with “high temp” and off with “low temp”? If so the PID will not work. Or do you using a KTY / similar? http://support.automation.siemens.com/WW/view/en/26447106 |