Hello Friends; I'm trying to transfer a project to a MP 277 10" Touch (6AV6 643-0CD01-1AX1), but It's requesting a password when I click on the "Panel Control" to configurate the transfer settings, and I don't have it. Is there any another way to proceed the transfer? If It is not possible, how can I reset It to a factory settings? Thanks. ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 11/21/2024 22:45:40New subject after splitting |
|
12/3/2024 2:19 PM | |
Joined: 8/3/2009 Last visit: 9/12/2025 Posts: 16409 Rating:
|
Hello Dan2712 You can do a Reset to factory settings (for MP277 you need a PPI MM Cable for this): https://support.industry.siemens.com/cs/ww/en/view/19701610 But Also a nomal OS Update should clear the PW settings (but of course a transfer has to be possible to perform an OS Update, so depends on which settings are active on the Panel) Bye Murof |