good afternoon, i need your help. i have a V20 3kw on a water pump for constant pressure system via press sensor 4-20mA 2-wire. i dont know how to make it work. which are the parameters to adjust the sensor in order to display in bar between 1 and 10 and give reference to the drive so it can work in constant pressure ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 1/14/2016 9:18:42 AMNew subject after splitting |
|
| 1/14/2016 9:49 AM | |
|
Joined: 8/31/2013 Last visit: 11/2/2025 Posts: 608 Rating:
|
Hey Here in the Attachment you can find the suitable guide for your application You should activate the PID in your inverter Attachment63.pdf (1079 Downloads) |
|
Warm Regards |
|