Hi there, regarding the overflow message, perhaps the content from this FAQ might be helpfull: https://support.industry.siemens.com/cs/ww/en/view/109973555 And about the "Changes to the technology object cannot be applied in RUN" message: If there is a change at any motion technology object (check the icons in the project tree on the left when you're online on the PLC), and the TO is active on the PLC, then you cannot download this change, therefor this message. If this appears without any difference at a TO, but only with differences at other DBs/FC/whatever, then it might be, that the change done there leads to a change in an instance-DB that inherits an MC_Power instruction of a TO that is currently active. In short: You can also not download a change that affects MC_Power of a currently active TO. If none of this is the cause, well then we'll have to check closer, I guess. But then my suggestion would be to contact customer support about this. Provide information what you changed and where, provide the project and information about the error that appears, as well as the used versions of TIA Portal and the firmware on the PLC. Regards, |