(0)| 3/5/2025 3:29 PM | |
|
Joined: 3/27/2020 Last visit: 8/25/2025 Posts: 10 Rating:
|
Hi Everyone, I have some questions regarding communication between PLC. Currently we have a systems running with 4 PLC S7-1516F. We configure it as such : - PLC A (X1 Interface is IO controller) - PLC B (X1 Interface is IO Controller and X2 Interface is IO Device) - PLC C (X1 Interface is IO Controller and X2 Interface is IO Device) - PLC D (X1 Interface is IO Controller and X2 Interface is IO Device) PLC A Communicate with PLC B, PLC C, and PLC D using X1 of PLC A and X2 on the other PLC. Since we are not allowed to have X1 and X2 interface with the same subnet, the local IO of PLC B, PLC C and PLC D is not visible from PLC A X1 Subnet. Looking at the diagram in manual, we assume we that need to separate between the interface that controls the IO and the interface that communicate with a higher level controller but the more I read into the manual, there's no mentions that I do need to separate it. Do I need to use X2 to communicate to a higher level controller or can I use X1 on my PLC B to communicate to the higher level controller and my local IO devices? Thank you all Below is the manual I've been using : https://support.industry.siemens.com/cs/ww/en/view/109478798 |
Last edited by: Moderator_Lan at: 03/05/2025 16:33:27link optimized |
|