(0)| 1/15/2014 4:44 PM | |
|
Joined: 7/7/2010 Last visit: 12/29/2025 Posts: 16333 Rating:
|
How many connections does that s7-1200 have? HMI, drives, profinet devices, remote I/O? I have to wonder if you are hitting a profinet limitation. To test that theory, you could disconnect an HMI and see. To get a better answer, you can of course send your question to Support Request |
|
science guy |
|
| 1/16/2014 3:12 PM | |
|
Posts: 10 Rating:
|
Hi did you try huggy's idea? please resert the PLC to factory default and dowload again...... let us know. |
Follow us on