Does the OPC UA server of the S7-1500 PLC (the latest V4.0) support the alarms of TOs/Technology Objects (e.g. PositioningAxis)? If yes, how to configure the server and the UaExpert client? Which node in the address space is to be added to the Event View? ------------------------------------------------------------------------------------------ |
Last edited by: Kristof Baksai-Szabo at: 11/27/2025 12:59:59Last edited by: Moderator_Lan at: 11/27/2025 13:47:20New subject after splitting |
|
| 11/28/2025 1:22 PM | |
|
Joined: 10/11/2006 Last visit: 12/22/2025 Posts: 6062 Rating:
|
Hello, it is not possible to activate an automatic transfer of the TO-alarms via OPC UA. It is necesarry to copy the alarms in a datastructure and transfer this data structure via OPC UA. General Examples: OPC UA methods for the SIMATIC S7-1500 OPC UA server - ID: 109756885 - Industry Support Siemens |
|