Dear Kthalji, For this case put the following parameters: P0700[1] = 2 P0701[1] = 1 "Function of DIN1: "On /Off" for remote start and stop" P1000[1] = 1
You can make P1080[1] = 40 "Minimum Frequency" Also have a look on the attached picture which descripe the timing diagram for both setpoint frqueny and P1080 and actual output frequency. Hope this helps. |
|
Ayman Elotaify |
|
| 11/5/2009 4:40 AM | |
|
Joined: 8/21/2008 Last visit: 7/25/2025 Posts: 141 Rating:
|
hi kthalji, I 100% agree with ayman. Please go through the attached document for more details. hope it will be useful to u. rgds, RBM
AttachmentDrive_command_data_sets.pdf (547 Downloads) |